I have a little quandary regarding a Inspection and test that I carried out over the last few days at a house that's been converted to flats
Now there's a CU that has a 30mA RCD main switch supplying the sub mains to the flats,,,,,, what code would you say???
IMHO... lets say that someone in the top floor flat receives an electric shock for some reason which trips the RCD.... now both the other flats lose power and the downstairs flat goes to the CU to investigate and sees that the RCD has tripped so he resets it...... unfortunately the occupant of the upstairs flat is still touching the cable/appliance that gave them a shock and gets another one .... so for me it's a C2 unless someone can convince me otherwise...
I realise that this would only get a C3 at most in a domestic,,, but that's usually under the control of a single occupant who you'd hope would investigate the cause
Now there's a CU that has a 30mA RCD main switch supplying the sub mains to the flats,,,,,, what code would you say???
IMHO... lets say that someone in the top floor flat receives an electric shock for some reason which trips the RCD.... now both the other flats lose power and the downstairs flat goes to the CU to investigate and sees that the RCD has tripped so he resets it...... unfortunately the occupant of the upstairs flat is still touching the cable/appliance that gave them a shock and gets another one .... so for me it's a C2 unless someone can convince me otherwise...