Evening all.
I am in need of some advice regarding remedial work I am in the process of carrying out following a PIR by the clients insurance company.
The site is a tourist attraction consisting of various lighting effects and waterfalls etc.
A 3 phase board feeds 8 other boards. All armoured cable (everything underground)
Basically it is stated within the report that
"Two circuits were supplied from ways 1 & 3. These should be supplied from seperatly protected supplies"
Having had a look at this, I have found that they are lighting circuits. 2 cables in each MCB, each supplying a lighting control box. Now I personaly don't see anything wrong with this. If they are connected to the same MCB then surely they are 1 circuit? The rating of the MCB is adequate for the size of cable. Is there a reg that confirms what they have stated??
also;
"Both submersible pumps where supplied via the same MCB. They should be split up onto 2 seperate supplies"
Ok. Now these pumps are controlled by a control box linked to the CPU that controls "the show". So, basically an MCB supplies the control box and then the 2 pumps are fed from the control box. Again I do not see an issue here.
also;
"There are 18 submersible pumps within the installation, they do not appear to be provided with overload protection. It is recommended that the rating be identified in order for the requirement for overload protection be detirmined."
Ok. Surely the 10A MCB feeding the control box that the pumps are connected to provides adequate overload protection?
Any advice/opinions appreciated chaps!
GS
I am in need of some advice regarding remedial work I am in the process of carrying out following a PIR by the clients insurance company.
The site is a tourist attraction consisting of various lighting effects and waterfalls etc.
A 3 phase board feeds 8 other boards. All armoured cable (everything underground)
Basically it is stated within the report that
"Two circuits were supplied from ways 1 & 3. These should be supplied from seperatly protected supplies"
Having had a look at this, I have found that they are lighting circuits. 2 cables in each MCB, each supplying a lighting control box. Now I personaly don't see anything wrong with this. If they are connected to the same MCB then surely they are 1 circuit? The rating of the MCB is adequate for the size of cable. Is there a reg that confirms what they have stated??
also;
"Both submersible pumps where supplied via the same MCB. They should be split up onto 2 seperate supplies"
Ok. Now these pumps are controlled by a control box linked to the CPU that controls "the show". So, basically an MCB supplies the control box and then the 2 pumps are fed from the control box. Again I do not see an issue here.
also;
"There are 18 submersible pumps within the installation, they do not appear to be provided with overload protection. It is recommended that the rating be identified in order for the requirement for overload protection be detirmined."
Ok. Surely the 10A MCB feeding the control box that the pumps are connected to provides adequate overload protection?
Any advice/opinions appreciated chaps!
GS