Hi
Went to property today to do EICR that has x3 DB's,
DB1 with x7 mcb's, 80a 100mA Earth leakage circuit breaker on a TT system with 6mm earthing conductor, 6mm water bonding.
DB2 with x2 mcb's 100a 30mA RCD MS feeding shower & electric heater on TNCS system with 16mm earthing conductor.
DB3 with x6 mcb's 100a MS feeding night storage heaters on TNCS system with 16mm earthing conductor.
I am aware that you should not have 2 different types of earthing system within domestic property, so i have asked her to contact electricty supplier to check if PME system available. She has done this but dont know how long we will have to wait! I done some tests whilst on site. DB1 Ze 83.5 ohms DB2 Ze 0.36 DB3 Ze 0.38. Although DB2 & 3 Ze slightly high (have seen higher readings accepted by supplier in the past) all 3 boards have fairly good earth paths.
If PME available, then easy to convert DB1, but would need to upgrade main earth & water bonding. customer wants house made safe so is willing for me to carry out any required work.
Prob i have is that i contacted Part P scheme help line with no real help regards EICR code! whilst i wait to hear back from supplier.
What do you guys think??
Thanks
All 3 DB's are side by side
Went to property today to do EICR that has x3 DB's,
DB1 with x7 mcb's, 80a 100mA Earth leakage circuit breaker on a TT system with 6mm earthing conductor, 6mm water bonding.
DB2 with x2 mcb's 100a 30mA RCD MS feeding shower & electric heater on TNCS system with 16mm earthing conductor.
DB3 with x6 mcb's 100a MS feeding night storage heaters on TNCS system with 16mm earthing conductor.
I am aware that you should not have 2 different types of earthing system within domestic property, so i have asked her to contact electricty supplier to check if PME system available. She has done this but dont know how long we will have to wait! I done some tests whilst on site. DB1 Ze 83.5 ohms DB2 Ze 0.36 DB3 Ze 0.38. Although DB2 & 3 Ze slightly high (have seen higher readings accepted by supplier in the past) all 3 boards have fairly good earth paths.
If PME available, then easy to convert DB1, but would need to upgrade main earth & water bonding. customer wants house made safe so is willing for me to carry out any required work.
Prob i have is that i contacted Part P scheme help line with no real help regards EICR code! whilst i wait to hear back from supplier.
What do you guys think??