[quote name='Andy
Compliance with the wiring regulations will go a long way to proving competence, should there be any dispute, and is far from being a 'John Wayne' attitude.and you are making a statement that they are legally binding documents?do what you want,
I'll laugh when you go to court and try to use that as a defence for killing some innocent person through your incompetence
typical of the dont care just pay me attitude that is dragging our trade down, while everyone else suffers due to your john wayne attitude.
as you say GUIDANCECompliance with the wiring regulations will go a long way to proving competence, should there be any dispute, and is far from being a 'John Wayne' attitude.As the 'diagram' is scanned from 'Guidance Note 8', and the leaflet is from the IEE 'Wiring Matters', I would say that they comply with the 'Regs'.
How can you expect anyone to take your theories about running an earth to an outbuilding above the guidance given by electrical engineers - you really are funny!
And I've just Googled 'innocent person killed through tn-c-s earth to outbuilding' - and guess how many hits I got? ?:|..... a defence for killing some innocent person through your incompetence
If there are lots of instances where it is not PME, you should contact the DNO responsible, and point out that they are in breach of ESQCR2006.because its not,its distributed by a concentric cable, and unless you live in an inner city there are lots of instances where its not PME, and if it is then why are my PFC readings so different?
the resistance between N&E on a true PME should be neglible, its the same cable spiked all the way back to star point,
do I need to do a drawing to show how PME differs from TNCS.?
places with their own 11KV transformer may be TNCS, but not PME. DNO is not in breach of ESQCR.If there are lots of instances where it is not PME, you should contact the DNO responsible, and point out that they are in breach of ESQCR2006.
I dont have an ESQCR about at the minute so if you want to quote me the reg I'll happily read it,If the DNO is distributing the TN-C-S without PME, then they are in breach of Regulation 9(2) of ESQCR2002.If the equipment belongs to the consumer, then they are in breach of Regulation 8(4) of ESQCR2002, and the DNO is in breach of Regulation 9(4) of ESQCR2002.
Either way the DNO is in breach of ESQCR2002.
I believe spin is refering to the following passeges:I dont have an ESQCR about at the minute so if you want to quote me the reg I'll happily read it,but would that be similar to saying a 6mm earth is unacceptable simply because it doesnt comply with BS7671/2008, but was fine under 15th.?
I dont know, I'm only asking.
Section 9 is only relevent where PME conditiona apply so if its not PME then section 9 will not apply (although I fail to see how the reference to 9(4), i.e. a caravan or boat, is applicable). Also its unlikely 8(4) will apply either as if they have been conbined, it was probably done by the DNO even if it was done on the consumers equipment.General requirements for connection with earth8. - (1) A generator or distributor shall ensure that, so far as is reasonably practicable, his network does not become disconnected from earth in the event of any foreseeable current due to a fault.
(2) A generator or distributor shall, in respect of any high voltage network which he owns or operates, ensure that -
(3) A generator or distributor shall, in respect of any low voltage network which he owns or operates, ensure that -
- (a) the network is connected with earth at, or as near as is reasonably practicable to, the source of voltage but where there is more than one source of voltage in that network, the connection with earth need only be made at one such point;
(B) the earth electrodes are designed, installed and used in such a manner so as to prevent danger occurring in any low voltage network as a result of any fault in the high voltage network; and
© where the network is connected with earth through a continuously rated arc suppression coil, an automatic warning is given to the generator or distributor (as the case may be) of any fault which causes the arc suppression coil to operate.
(4) A consumer shall not combine the neutral and protective functions in a single conductor in his consumer's installation.
- (a) the outer conductor of any electric line which has concentric conductors is connected with earth;
(B) every supply neutral conductor is connected with earth at, or as near as is reasonably practicable to, the source of voltage except that where there is only one point in a network at which consumer's installations are connected to a single source of voltage, that connection may be made at that point, or at another point nearer to the source of voltage; and
© no impedance is inserted in any connection with earth of a low voltage network other than that required for the operation of switching devices or of instruments or equipment for control, telemetry or metering.
(5) Paragraphs (1) to (3) shall not apply to a network which is situated within a generating station if, and only if, adequate alternative arrangements are in place to prevent danger.
Protective multiple earthing
<A name=9>9. - (1) This regulation applies to distributors' low voltage networks in which the neutral and protective functions are combined.
(2) In addition to the neutral with earth connection required under regulation 8(3)(B) a distributor shall ensure that the supply neutral conductor is connected with earth at -
(3) Paragraph (2)(a) shall only apply where the supply neutral conductor of the service line referred to in paragraph (2)(a) is connected to the protective conductor of a consumer's installation.
- (a) a point no closer to the distributor's source of voltage (as measured along the distributing main) than the junction between that distributing main and the service line which is most remote from the source; and
(B) such other points as may be necessary to prevent, so far as is reasonably practicable, the risk of danger arising from the supply neutral conductor becoming open circuit.
(4) The distributor shall not connect his combined neutral and protective conductor to any metalwork in a caravan or boat.
But ahead of that the whole of section 9 only applies to PME networks. The distinction of TN-C is only made when referring to TN-C-S supplied from PME rather than TN-S supplied from a PME network.Sorry, I don't want to be seen as argumentative.However the Regulation applies whenever the distribution is TN-C, or as stated at the start of the Section, when "the neutral and protective functions are combined."
I'm sorry Ian, but what exactly does your statement mean?But ahead of that the whole of section 9 only applies to PME networks. The distinction of TN-C is only made when referring to TN-C-S supplied from PME rather than TN-S supplied from a PME network.
I think you misunderstand the Regulation.I think you misunderstand what I am saying. If a network is PME then this section is relevent and 9(1) just states that its only relevent for TN-C-S presentations on PME not something else (Like TN-S or TT).
Thats not how its written. If the network is not PME then 9 is not applicable at all.I think you misunderstand the Regulation.This Regulation informs when PME is required, and that is whenever the distribution is TN-C.
The heading is: "Protective Multiple Earthing."Thats not how its written. If the network is not PME then 9 is not applicable at all. The logic is simple.
First decision, is it PME [YES|NO].
If YES then continue to itterate this section.
If NO then continue to section 10.