Todays job was to provide a cooker circuit from a cu with a 30mA rcd protecting the entire board.
Looked simple at the outset except that I will have to run SWA around building as no direct access from within.
The building is an annex to the main house however the cutout is within this annex.
The cutout feeds 2 x cu each with a 63A mcb which inturn supply the house and annex electrics.
The 2 cu's are metal and the supply to house and annex are via 16mm T&E.
No additional protection to these tails and no front end RCD (It's a TT system).
Would you: Proceed with the cooker circuit and make note on EIC that tails etc are not up to standard?
Install front end 100mA TD rcd?
Change metal cu's for insulated?
Looked simple at the outset except that I will have to run SWA around building as no direct access from within.
The building is an annex to the main house however the cutout is within this annex.
The cutout feeds 2 x cu each with a 63A mcb which inturn supply the house and annex electrics.
The 2 cu's are metal and the supply to house and annex are via 16mm T&E.
No additional protection to these tails and no front end RCD (It's a TT system).
Would you: Proceed with the cooker circuit and make note on EIC that tails etc are not up to standard?
Install front end 100mA TD rcd?
Change metal cu's for insulated?