Yes I do, and to be honest is the only way you could do it notwithstanding all regulations. One point though, remember those touch voltages, they are a pain to achieve with normal T&E cable.Not wrong M,Just not my way of thinking.
BTW do you "agree" with my thoughts?...
Care to enlighten us with your suggestions?I was wrong, with my suggestions, so if anyone wants to beat up a mod, then have a go at replying to this thread.
Of course I will, i thought that the clue in the description was the statement that the distance from the stop tap, hence the water intake was 6m away as the crow flies, now to me I would argue that the disruption and extra costs of getting a suitable bond to this either inside or outside of the property, would be equally served if the bonding was done local to the CU. My reasons being that the connections could be easily identified, located and tested. They would not suffer from fauna and other influences (external), and as long as the certificates noted the position of the bonds, it would still comply to the regulations.Care to enlighten us with your suggestions?
The later half of 2.3 seems to say only what you install needs to comply?Assuming the job is not in Scotland,Approved Document P, Section 2, 2.1
Where any electrical installation work is classified as an extension, the addition & alteration work must include:
a) such works on the existing fixed electrical installation in the building as are necessary to enable.....
the addition/alteration (the extension) ;
the circuits which feed it;
the protective measures &
the relevant earthing and bonding systems..........
....to meet the requirements
AND....
B) Establishing that the mains supply equipment is suitable.
So all four items listed above have to meet the requirements of the current regs........the 100 mA up-front RCD doesn't, and neither will a RCD fused spur......what about RCD protection for the rest of the circuit?
2.3The later half of 2.3 seems to say only what you install needs to comply?
Not sure what you mean by 'beyond the requirements' - Building Regs are statutory, 7671 isn't.Ok so would you say this goes beyond the requirements of 7671?
It's the actual 'building regulation' they're referring to, not the approved document.What page is 4(2) on?
I'll give you this one - kind of contradicting itself really, isn't it.This is in the notes of application.
Regulation 4(2) also means that, when extending
or altering an installation, only the new work
must meet current requirements and there is no
obligation to upgrade the existing installation
unless the new work would adversely affect the
safety of the existing installation, or the state of
the existing installation was such that the new
work could not be operated safely, or where there
is a requirement to upgrade imposed by the
energy efficiency requirements of the Building
Regulations.
This to me is saying earthing and bonding is to meet meet 7671 and my additional part of circuit and not the existing?
Some think this way, where others tend to think - 'if you've worked on a circuit, you're responsible for it' - it's another 'grey' area that causes a lot of confusion.Sorry I wasnt very clear there, iv always thought main bonding and earthing sound im ok to make a addition to a circuit as long as what i do complies, no need to upgrade whole circuit to the 17th edition, following guidance from ESC.
Job not done yet gs.As far as the bonding goes, I would agree with ADS' post (no 15). But I assume this is not the route you have decided to take Side?You said that the boiler is on the ground floor? What is above the boiler? as in on the 1st floor?
Cheers.
GS
Well I don't read it that way, nor do I do it that way!So you mean a sparky goes to a house and adds a socket, does it properly and they are now responsible for the whole of the old installation ?