max demand and diversity
james KEI
May 21, 2011
46
hi all
just wanted to get some opinions. got a place being converted in to two flats and everything will be electric! new edf supplie(s) to go in and so need to know what max demand in kva is for edf to evaluate.
just one flat
electric shower 10kw
electric oven/hob 8kw
electric water htr 3kw
storage heaters for main heating 3x 2.5kw & 1x 3.4kw
and then the usual couple of rings and lighting circuits.
using the onsite guide for diversity values I come out at 176A
even with a g factor of 0.8 (playing it safe) it's still 140A. customer is thinking there wont be a economy 7 supply so it'll all be on one supply.
not had much experience where everything is electric so looking for some views from people that have and what the scenario has been to get over the large load. 3phase seems a bit ott?? is there a larger supply available than 100A single phase although then i guess DB's etc aren't rated high enough. i realise that in real life it shouldn't pull near to 140a but thats what it is coming out at on paper and if it went wrong with me saying less than 140A i'd cop the blame which i don't want.
thanks for any help
Economy 7 normally all comes up the same supply cable, but as the storage heaters take most power at night when most other appliances are off they are not all additional to things like showers and cookers.
Read the posts...very interesting.
But what is the "g" factor?
Where would I find it or others?
Hi
Thanks for the replies. Sidewinder-can you tell me why you say to use 0.4? In the designers guide there's a graph (don't have it to hand) and it gives you the g factors depending on the possible coincidence all all loads. As there's to be NO economy 7 and the storage heaters will be off the general supply (the only supply) I chose a high coincidence which came out at 0.8.
---------- Post Auto-Merged at 18:51 ---------- Previous post was made at 18:50 ----------
Storage heaters by their very nature store up heat over one period of time then release that heat over another period of time. Irrespective of if they are paying economy 7 rates or not, I would think that storage heaters will be on during the night and outputting heat during the day. I can't imagine anyone switching them on to store during the day and release heat at night? Are the definitely storage heaters? or are they combined storage and radiant heater?
Hi doc
It's planning for a house to be converted in to two flats so nothing there as yet. True, but as there is no eco7 there's nothin to stop them turning them on in the day. Unless I introduce my own version with a time clock and contactors.
Has noone come across this situation before?
IF you are going to allow for true 24hr electric heating then you cannot allow diversity on that at all.
"Officially".
However, you said storage heating in your op.
James, can you put the name of the publication in a post?
I have never heard the term "coincidence factor" but I can
imagine exactly how it might be used.
Hi docIt's planning for a house to be converted in to two flats so nothing there as yet. True, but as there is no eco7 there's nothin to stop them turning them on in the day. Unless I introduce my own version with a time clock and contactors.
Why would someone want to turn a storage heater on during the day, as they are not an instantaneous heat source? The logic of such usage would be similar to using an electric shower to fill a bath, very long winded and inefficient. A person wanting to turn heat on/off during the day would not opt for storage heaters. I would suggest a reassessment of exactly what is needed by the client to ensure the correct type of heating is installed. Once you have verified the correct type of heating the max demand can be reassessed. Dimplex do a good range of heaters capable of supplying daytime operation at lower power ratings.
Table 3.4 g factors table pg34
Figure 3.4 coincidence g factor graph pg33
In the electrical installation design guide