I am just about to finish my second assesment and i am stuck on a few questions. I think I know the answer but not sure. So...the questions are:
1) The proposed design of the installation includes the following protective devices:
BS EN 60898 type d mcb for the MIG welder (rated 16A)
MCCB rated @ 125A for the distribution circuit to the DB2.
Determine using manufacturer's information whenever discrimination will be achieved
2) determine the minimum size of cpc for each of the circuits giving consideration to disconnection times and thermal constraint.
circuit 1: 5kW/400V 3 phase machine; actual Zs=0.59ohms; Ia=430.10A
circuit 2: 12kW/400V 3 phase machine; actual Zs=0.5ohms; Ia=800A
circuit 3: 11kW/400V MIG Welder actual Zs=0.5ohms; Ia=800A
circuit 4; 3kW/230V water heater (i did not work this out yet)
3) Circuit 4 should be wired in MI cable for the total lenght or the circuit? Can I run the MI cable in the same trunking with the other 3 circuits above applying the corection factor Cg of 4 cables or in a separate containment?.
I also had a go on the questions and I come up with this:
1) the discrimination will not be achieved because the 16A circuit breaker has higher breaking capacity due to high staring currents (type D)
2)using the adiabatic equation circuit 1 has 1mm cpc cable & 1.5mm live conductors
circuit 2 has 6mm cpc cable & 6 mm live conductors
circuit 3 has 6mm cpc cable & 4 mm live conductors
For the calculation I used the t=0.4 ses K=115
S=(square root of)I squared X t all divided by K
Help and sugestions are well come.
Thank you very much
Alextrician
I am just about to finish my second assesment and i am stuck on a few questions. I think I know the answer but not sure. So...the questions are:
1) The proposed design of the installation includes the following protective devices:
BS EN 60898 type d mcb for the MIG welder (rated 16A)
MCCB rated @ 125A for the distribution circuit to the DB2.
Determine using manufacturer's information whenever discrimination will be achieved
2) determine the minimum size of cpc for each of the circuits giving consideration to disconnection times and thermal constraint.
circuit 1: 5kW/400V 3 phase machine; actual Zs=0.59ohms; Ia=430.10A
circuit 2: 12kW/400V 3 phase machine; actual Zs=0.5ohms; Ia=800A
circuit 3: 11kW/400V MIG Welder actual Zs=0.5ohms; Ia=800A
circuit 4; 3kW/230V water heater (i did not work this out yet)
3) Circuit 4 should be wired in MI cable for the total lenght or the circuit? Can I run the MI cable in the same trunking with the other 3 circuits above applying the corection factor Cg of 4 cables or in a separate containment?.
I also had a go on the questions and I come up with this:
1) the discrimination will not be achieved because the 16A circuit breaker has higher breaking capacity due to high staring currents (type D)
2)using the adiabatic equation circuit 1 has 1mm cpc cable & 1.5mm live conductors
circuit 2 has 6mm cpc cable & 6 mm live conductors
circuit 3 has 6mm cpc cable & 4 mm live conductors
For the calculation I used the t=0.4 ses K=115
S=(square root of)I squared X t all divided by K
Help and sugestions are well come.