The RCD and mcb in the house CU for the kitchen ring will provide all the protection you need for your armoured cable. The FCU will only provide a means of isolation if you ever wanted to make it dead without affecting the kitchen sockets which i think is a good idea if its easier eniugh to install without making too much mess but still not necessary. You keep mentioning extra protection for the armoured but it's just an extension of the kitchen ring. Those cables don't have 'extra' protection do they?
Garage CU- It's a 63amp main switch not 63mA and it doesn't need to be an RCD main switch in the garage as the circuits are already protected by RCD in the house.
Are you going to provide a test cert with this?
Why you upgrading the 16amp mcb to 20amp? What are they going to be using in this garage? With a battery charger and drill it will be less than 5 amps.
Garage CU- It's a 63amp main switch not 63mA and it doesn't need to be an RCD main switch in the garage as the circuits are already protected by RCD in the house.
Are you going to provide a test cert with this?
Why you upgrading the 16amp mcb to 20amp? What are they going to be using in this garage? With a battery charger and drill it will be less than 5 amps.